Good update here - It's finished! And boy was it a lot of work. I just had one minor issue with the enclosed contactor and everything else went smoothly.
As a reminder of what's going on (it's a lot) from the previous post:
View attachment 30446
I pulled 4/0 to the big manual disconnect, and then to the RPC control panel.
The RPC panel is a nasty mess of wires because I wanted to leave a bit of wire in case the panel ever needed moved (I seriously hope not).
The motor wiring has a good bit going on. There's 9 wires to the motor, and 3 hots and a ground coming into the pecker head from the RPC panel. That's a lot of wires to wrangle. The motor connections all come terminated with ring terminals, and American Rotary supplies bolts/lock nuts for bolted connections. I'm not a fan, so let's do one better - Polaris gray connectors.
But first we need to run some wire to it. Because I'm using 2" conduit and the motor junction box only came with a hole large enough for something smaller than 2", so it's time we opened up the hole in our pecker box (heh). Luckily, we have the technology.
I wish I would have gotten pictures of how I clamped this thing to the front of the Bridgeport table - but that's what happened and I extended the gantry nearly all the way out and swung it to the side to reach. Use a boring head to cut it a little larger and we have something we can use.
Back to the wiring. I did wire it initially with the bolted connections just to make sure everything was functional. No sense in causing a fuss in case something was screwy with the motor. But then I went back and chopped those ring terminals off and used Polaris connectors:
Don't forget the vibration isolating feet!
Now that we have the manufactured 3rd leg for 3 phase (woohoo!), let's send it places. First, that's the enclosed contactor. This was fairly simple, I put it next to the RPC panel and ran the 3 hots/ground/2 monitor wires through. Here's the panels before the conduit went in (RPC panel on the right, enclosed contactor on the left):
Here's where I ran into the issue with the enclosed contactor. [For anyone searching this is an EC-90150 enclosed contactor. Information for these as-installed is nearly impossible to find so maybe this will help someone out.]
Voltage on the output side was FLAKY - and I could change it's behavior by moving the output side lugs. I made a video for American Rotary during troubleshooting, and they confirmed what I suspected - missing bolts between the contactor (upper) and overload monitor (lower) modules.
That was resolved with some bolts and belleville washers, and all is well now.
From the enclosed contactor we go to the transformer.
We have 3 contact areas - Input, taps, and outputs. Inputs aren't variable, so that's easy, just connect the incoming hots to X1, X2, and X3.
The outputs are fairly simple because I want 400/230V, so that means I need to connect H0-H4-H5-H6.
The taps require a little more thinking. Under no load conditions, I have higher than nominal (240V) voltage. But, based on experience pulling moderate load I know the voltage drops a few volts to just under 240V (typically). For right now, I've left the taps on the 240V setting, but this will be one thing I monitor very closely at first and may need to change.
If you watched the video, you can hear how quickly the motor starts up. It is seriously impressive that a 75hp motor tipping the scales at 600lbs comes to full speed in ~1 second. My clamp meter died somewhere between the end of racing season and now, so I haven't been able to check in-rush current. I'm really curious what that looks like for both the motor and transformer, so I have a new meter arriving tomorrow to measure it. I haven't tripped the 200A breaker, so the RPC soft start capacitors seem to be doing some work.
And things are...progressing

Taking some time to clean the coolant/conveyor systems, as well as the machine itself.